Yes, you can use any value you like. WinterDesignDay with a zero daily
range
will keep a constant temperature as will SummerDesignDay. So yes,
you can set a 30C max with 0 temp range. You can call it SummerDesignDay
but you need to make sure that your schedules do what you want them to
do on SummerDesignDay. If you need a "summer sun" position, use an
appropriate date (depending on latitude).
Start-->All Programs-->EnergyPlus V1-2-2 Programs-->DocMainMenu
Search on Design Days (pg 25, 55 of the InputOutputReference).
Also look at discussion of WinterDesignDay and SummerDesignDay
under Day Type in Schedules (pg 45, 78 of the pdf).
"deserteagle_zhou"
<yp5166@xxxxxxx> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent by: cc:
EnergyPlus_Support@yaho Subject: [EnergyPlus_Support] Re: outside air temperature
ogroups.com
09/29/2005 09:34 PM |--------------------------|
Please respond to | ( ) Federal Record |
EnergyPlus_Support | (*) Not a Federal Record |
|--------------------------|
User Filed as: Not Categorized in ERMS
------------------------------------------------------------------------------------|
| |
| If this external e-mail is a record and you are the first EERE recipient, click the|
| 'File to ERMS' button in the toolbar to categorize this e-mail |
------------------------------------------------------------------------------------|
Thank you , Dru,
Because I am testing a cooling mode for a certain equipment, I need
a fixed outdoor temperature 30DBC . Then can I use SummerDesignDay
in Day Type instead of WinterDesignDay to accomplish this task? OR
WinterDesignDay can handle any temperature I want, i.e, -10C or 30C?
"Whatever" means I can customize a value I like, does not it?
John
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Drury.Crawley@e... wrote:
>
> John,
>
> You could create a weather file with timestep data--starting
> with a CSV--but EnergyPlus interpolates between the hourly
> data automatically. So that if two hours have the same
temperature,
> the intermediate timesteps would as well. The easiest way
> would be to take the one line (hour) of data that you want to
> set as your condition the entire year and duplicate that 8759
> times. If you only copied the data to the right of the
> month/day/hour/minute
> fields, it should be OK.
>
> But has Linda Lawrie noted, you can also use the design days
> to do that--the Winter design days do just that.
> Set maximum temperature to whatever, and daily range to 0.
>
> Search for Design Days in the documentation.
>
> Dru Crawley
>
>
>
>
>
> "deserteagle_zhou"
> <yp5166@1...> To:
EnergyPlus_Support@xxxxxxxxxxxxxxx
> Sent by:
cc:
> EnergyPlus_Support@yaho Subject:
[EnergyPlus_Support] Re: outside air temerature
>
ogroups.com
>
>
> 09/29/2005 09:23
AM
> Please respond
to
>
EnergyPlus_Support
>
>
>
>
>
> Dear Crawley,
>
> That is really a good way. But in this csv file, I can only change
> hourly temperature data. How about changes in each timestep,say,10
> minute ?
> Do data within a timestep come from interpolation?
>
> Acatually I wanna let the building load constant all the day. Now I
> see it impossible because of too many kind of data needed to
change.
>
> Thank you
>
> John
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Drury.Crawley@e...
wrote:
> >
> > Convert your EPW to a CSV (E+ format) using the WeatherConverter.
> > Modify the temperatures there (CSV), then convert back to EPW.
> >
> >
> >
> >
>
> > "deserteagle_zhou"
>
> > <yp5166@1...> To:
> EnergyPlus_Support@xxxxxxxxxxxxxxx
> > Sent by:
> cc:
> > EnergyPlus_Support@yaho Subject:
> [EnergyPlus_Support] outside air temerature
> >
> ogroups.com
>
> >
>
> >
>
> > 09/28/2005 10:15
> AM
>
> > Please respond
> to
>
> >
> EnergyPlus_Support
>
> >
>
> >
>
> >
>
> >
> >
> >
> > Hi,everybody,
> >
> > Is there a way to make the outdoor temperature as a constant
value
> in a
> > E+ whole-day run? I opened the epw file, and it seemed not
> possible to
> > acheieve manually.
> >
> > Thank you!
> > John
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
> appropriate
> > folder in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf
> and press
> > the "search" button.
> >
> >
> >
> >
> >
> SPONSORED LINKS
> >
> > Cad software Maintenance program Email software
> > program software program
> >
> > Backup software Medical software program Wedding program
> > program software
> >
> >
> >
> > YAHOO! GROUPS LINKS
> >
> > Visit your group "EnergyPlus_Support" on the web.
> >
> > To unsubscribe from this group, send an email to:
> > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> >
> > Your use of Yahoo! Groups is subject to the Yahoo! Terms
of
> Service.
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
appropriate
> folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf
and press
> the "search" button.
>
>
>
> YAHOO! GROUPS LINKS
>
> Visit your group "EnergyPlus_Support" on the web.
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> Your use of Yahoo! Groups is subject to the Yahoo! Terms of
Service.
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate
folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press
the "search" button.
YAHOO! GROUPS LINKS
Visit your group "EnergyPlus_Support" on the web.
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.
------------------------ Yahoo! Groups Sponsor --------------------~-->
Most low income households are not online. Help bridge the digital divide today!
http://us.click.yahoo.com/cd_AJB/QnQLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/