This is a good start. I would also add some cross mixing to transfer air
between the two zones. What flow rate to use? That is very difficult to say.
Note that windows in EnergyPlus are opaque to infrared (long-wave) radiation
(see Engineering Reference p. 171, pdf p. 199), so there is no direct radiant
exchange between surfaces in different zones even when there is an interior
window. This should be a small effect if the windowglass is given a high
emissivity so that is will simply exchange with Zone A on one side, conduct
through and exchange with Zone B on the other side.
Also, be sure to use FullInteriorAndExterior solar distribution (in the
BUILDING object) so that beam solar can be transmitted through the partition
windows into the adjacent zone.
Mike
On 26 Sep 2005, at 9:24, dan_grunbaum wrote:
> Hi there,
>
> I am attempting to model zones which do not have partitions seperating
> them however they are kept at different conditions. To do this I have
> modelled them with partitions, however i have attached windows to the
> partitions which are nearly completely transparent to solar, visible
> and long wave length radiation and with a high conductivity. Is this
> the best way to model this situation or should I be doing something
> else ?
>
> Regards,
>
> Dan
>
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
Get Bzzzy! (real tools to help you find a job). Welcome to the Sweet Life.
http://us.click.yahoo.com/A77XvD/vlQLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/