Re: [EnergyPlus_Support] Simutanuous heating and cooling
My apologies for the delayed response . . .
In this model, the heating and cooling coil controllers both use the supply fan
outlet as the Control Node. This "downstream" control can cause the situation
you describe, especially in a VAV system, due to small inaccuracies in control.
An alternate approach is to use the SET POINT MANAGER:MIXED AIR to place a fan-
heat-adjusted setpoint on the mixed air node (which it currently is) and the
heating coil outlet node and the cooling coil outlet node. This would then
require changing the controller objects to use the coil outlet node as the
control node. This should give better control and eliminate the battling of
the heating and cooling coils.
Mike
On 11 Oct 2005, at 22:37, zhaicq98 wrote:
> I am simulating a VAV system. There is a heating and cooling coil in
> the air handling unit. When I ran the simulation and look at the
> heating and cooling coil load, I found something strange. During winter
> design day, the heating coil heats the air a bit hotter than what is
> needed, and then the cooling coil needs to bring the air temperature
> back to the setpoint. The load on the cooling coil is small though. I
> could not figure out what is going on. I have uploaded the input file
> to the "problem submittal" area under "files", with the name
> simutanuous heating and cooling.idf.
>
> Thanks for your attention. I am looking forward to your response.
>
> -Chaoqin
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
------------------------ Yahoo! Groups Sponsor --------------------~-->
Fair play? Video games influencing politics. Click and talk back!
http://us.click.yahoo.com/T8sf5C/tzNLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/