Re: [EnergyPlus_Support] 2 unitary groups



My apologies for the delayed response . . .

One should ask first whether there is any benefit in modeling two identical 
system serving the same zone.  

If the two are independently controlled and serving the same thermal zone, then 
there will be no difference in simulated energy use between two units of size X 
serving the same zone vs. one unit of size 2X serving that zone.  

If the two units act as stage one and stage two, where the second unit does not 
come on until the first unit is fully loaded, then there is a benefit in 
modeling two units.  To serve a zone with two systems, there should be only one 
CONTROLLED ZONE EQUIPMENT CONFIGURATION object for that zone.  There would then 
be multiple inlet node names, and the zone equipment list would list more than 
one piece of equipment.  Note that EnergyPlus allows only one AIR PRIMARY LOOP 
to serve a zone, so one or both of the systems must be zonal equipment such as 
the window air conditioner.

Mike




On 11 Oct 2005, at 22:43, dust_broom wrote:

> Hi
> 
> I woul like to know if its possible to have 2 equal unitary groups 
> controling the same zone at the same time! I'm asking because I've 
> already tried but it didn't work, it said that the zone node cannot be 
> repeted in the zone controled configuration.
> 
> Best regards, Emanuel
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




------------------------ Yahoo! Groups Sponsor --------------------~--> 
Most low income households are not online. Help bridge the digital divide today!
http://us.click.yahoo.com/cd_AJB/QnQLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/