Dear Sankar,

thank you for the fast response. 
The problem is that we actually use exactly such a system like you 
have described:
We have on the supply side of a cooling loop two parallel branches 
with a chiller in each branch. One of those chillers is served by a 
condenser loop with a cooling tower, and the other chiller is served 
by a condenser loop with a ground heat exchanger.
If I understood your explanations about multiple condenser loops, I 
think that such a system is possible to simulate.
But it doesn't work like we wont. The simulation crash always with 
the following error massage:

CalcConstCOPChillerModel: Condenser flow = 0, for 
ElectricChiller=LITTLE CHILLER GHE
**   ~~~   ** Occurrence info=80000_MÜNCHEN TMY2-999 WMO#=, 07/17 
01:00 - 01:30.

The mass flow calculation for the condenser loop served by the 
ground heat exchanger is zero, and I don't understand why. There is 
no reason, why the mass flow should be zero.
The condenser plant is on (availability), the mass flow rates for 
the pump, plant, chiller and ground heat exchanger are set.
The two chillers (one for the ground heat exchanger condenser loop 
and the other for the cooling tower condenser loop) are defined in 
the load range based operation object for the cooling loop and there 
is a cooling demand in the zones.
I have seen that such a problem was discussed by Micheal White and 
Mr. Ernest Tsang one year ago yet, but no solution for this problem 
was posted.

Name: 

Re: About condenser pump / airflow window
Nov 29, 2004 
5:23 pm

I will upload the zip version of my energy plus file to the files 
area, so you can have a look on the described problems (I think, 
there is some problem with the type of the chiller: constant COP)

I hope you can point us in the right direction toward the solution.

Best regards

Patrik





------------------------ Yahoo! Groups Sponsor --------------------~--> 
Most low income households are not online. Help bridge the digital divide today!
http://us.click.yahoo.com/cd_AJB/QnQLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/