[EnergyPlus_Support] Problem with CHILLER:CONST COP in Cooling Tower example



Dear Sankar,
I tested the example CoolingTower.idf which comes with E+1.2.3.
It runs without any problems in the delivered configuration (only one 
chiller is working). 
Now I tried to run 2 chillers in parallel, so I made the following 
changes: 
-) used 'All Chillers' instead of 'Electric Only' in the 'COOLING LOAD 
RANGE BASED OPERATION' object 'Peak Operation' and 'Off Peak 
Operation'
-) changed the order of equipments in the 'PLANT EQUIPMENT LIST' 'All 
Chillers': Now the 'Little Chiller' is the first element and the 'Big 
Chiller' is the second.

This results in following error:
   ** Severe  ** CalcConstCOPChillerModel: Condenser flow = 0, for 
ElectricChiller=LITTLE CHILLER
   **   ~~~   **  Occurrence info=CHICAGO_IL_USA ANNUAL COOLING 1% 
DESIGN CONDITIONS DB/MCWB, 07/21 07:10 - 07:20

Now this is very strange, because the AbsorbtionChilller.idf example, 
which have the same configuration, runs without any problems. The only 
difference is the used chiller type. The AbsorbtionChilller example 
uses a CHILLER:ELECTRIC in parallel to the CHILLER:ABSORPTION.

Therefore, I replaced the CHILLER:COP in the CoolingTower example with 
a CHILLER:ELECTRIC, and now the 2 chillers are working in parallel!!!

So it seems that the CHILLER:COP model have a problem to run in 
parallel with other chillers.


This is the same problem as reported by Patrik, an colleague at work, 
see post 'Re: How many condenser loops' from 21.Oct.2005. 
May be, the problem with CHILLER:COP is also the reason for the errors 
in the uploaded file chiller_09.30.2005.zip.

Christian











------------------------ Yahoo! Groups Sponsor --------------------~--> 
Get Bzzzy! (real tools to help you find a job). Welcome to the Sweet Life.
http://us.click.yahoo.com/A77XvD/vlQLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/