RE: [EnergyPlus_Support] Problem with CHILLER:CONST COP in Cooling Tower example



Hi Patrik and Christian,
 
>From your mail, It seems that there could be some thing wrong in the Constant COP chiller. I will look into the file uploaded by Patrik and check to see if the model is working properly. If not I will post a change request regarding the same so that it will be rectified.
 
Thanks for pointing out the potential bug
 
Sankar
S.K.Padhmanabhan
Research Associate
Mechanical & Aerospace Engineering
Oklahoma State University,
Stillwater, OK - 74075
Ph: (405)744-4380

________________________________

From: EnergyPlus_Support@xxxxxxxxxxxxxxx on behalf of christian1855
Sent: Fri 10/21/2005 6:23 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Problem with CHILLER:CONST COP in Cooling Tower example



Dear Sankar,
I tested the example CoolingTower.idf which comes with E+1.2.3.
It runs without any problems in the delivered configuration (only one
chiller is working).
Now I tried to run 2 chillers in parallel, so I made the following
changes:
-) used 'All Chillers' instead of 'Electric Only' in the 'COOLING LOAD
RANGE BASED OPERATION' object 'Peak Operation' and 'Off Peak
Operation'
-) changed the order of equipments in the 'PLANT EQUIPMENT LIST' 'All
Chillers': Now the 'Little Chiller' is the first element and the 'Big
Chiller' is the second.

This results in following error:
   ** Severe  ** CalcConstCOPChillerModel: Condenser flow = 0, for
ElectricChiller=LITTLE CHILLER
   **   ~~~   **  Occurrence info=CHICAGO_IL_USA ANNUAL COOLING 1%
DESIGN CONDITIONS DB/MCWB, 07/21 07:10 - 07:20

Now this is very strange, because the AbsorbtionChilller.idf example,
which have the same configuration, runs without any problems. The only
difference is the used chiller type. The AbsorbtionChilller example
uses a CHILLER:ELECTRIC in parallel to the CHILLER:ABSORPTION.

Therefore, I replaced the CHILLER:COP in the CoolingTower example with
a CHILLER:ELECTRIC, and now the 2 chillers are working in parallel!!!

So it seems that the CHILLER:COP model have a problem to run in
parallel with other chillers.


This is the same problem as reported by Patrik, an colleague at work,
see post 'Re: How many condenser loops' from 21.Oct.2005.
May be, the problem with CHILLER:COP is also the reason for the errors
in the uploaded file chiller_09.30.2005.zip.

Christian












The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.

Yahoo! Groups Links










[Non-text portions of this message have been removed]



------------------------ Yahoo! Groups Sponsor --------------------~--> 
Fair play? Video games influencing politics. Click and talk back!
http://us.click.yahoo.com/T8sf5C/tzNLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/