Regarding plenums. The 5-zone building is modeled with a plenum zone between
the roof and the ceiling of the occupied zones. If the return air for the
system flows through this space without return ducts, then this space is
designated as a return plenum in the system decription. This is the way
CompactHVAC-5ZoneVAVWaterCooled.idf is modeled, but this is not a requirement.
If the system has return ducts, then the system should be described with no
return plenum. This is the way CompactHVAC-5ZoneFurnaceDX.idf is modeled. In
conclusion, a return plenum is optional for both of these system types. I
would suggest that you try running these examples with and without a return
plenum to see the impace. If the plenum is exterior (as in these examples) I
would expect a signficant change in results. If the plenum is interior (such
as between middle floors in a tall building), I would expect the change to be
small.
Regarding chiller priority, the first chiller will run until the load exceeds
its capacity, then the second chiller will start while the first chiller
continues to run. So, yes, it means two chillers running at the same time,
when needed.
Mike
On 4 Nov 2005, at 3:59, eric_zhou1223 wrote:
>
> Hi£¬
> I am studing on the CompactHVAC example files shipped with E+.
> Is a " Return Plenum " an indispensable part in the VAV or Unitary
> AC equipment model?
>
> I checked the documentation, it says:
>
> "Field: Return Plenum Name
> Set to blank if no return plenum is to be modeled. If a return
> plenum is modeled, it must be
> modeled as a zone with surfaces, and the name of the plenum zone
> should be entered here."
>
> So I can conclude that modelling a return plenum may be not
> essential. Can a VAV system without a return-plenum modelling result
> in a big difference on the simulation results?
> And in the example file "CompactHVAC-5ZoneFurnaceDX", this field
> Return Plenum Name is left blank but it does include a return
> plenum. Is it a carelessness?
>
> Also,in Compact HVAC:Plant:chiller,for the last cell "priority", it
> means a sequential start-up operation.
> I just wanna be sure whether it implies two chiller running at same
> time, instead of an alternative action (when the second shifts in,
> the first quits )?
>
> Thank you for your help
>
> Eric
>
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
Get Bzzzy! (real tools to help you find a job). Welcome to the Sweet Life.
http://us.click.yahoo.com/A77XvD/vlQLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/