ISO 15099 says that in the absence of more detailed data (i.e., CFD,
experiment, etc.) outside wind speed should be used as an extreme condition.
The permeability probably refers to the natural convection model, which is
labeled (in ISO15099) Ah for the permeability of shading device itself, Al,
for the left side opening, etc. for Ar, Abot, Atop.
Charlie Curcija
-----Original Message-----
From: Peter G. Loutzenhiser [mailto:post@xxxxxxxxxxx]
Sent: Friday, November 11, 2005 8:17 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Shading calculations
Dear All,
Does anyone know how the calculations are made in EnergyPlus for an air gap
between a window and exterior shading device. I see this reference to
standard ISO 15099 (I am looking at the final draft) but when looking at the
standard, it says to assume a forced convection model and says to calculate
the airflow rate by using an experiment or CFD. But in EnergyPlus, there
are various inputs (side permuability, etc) that seem to indicate that it is
using some sort of model not described by the standard. I have the source
code, so if someone could kindly point me to correct subroutine or provide a
reference for this calculation, I would be most greatful!
Many thanks in advance.
Peter Loutzenhiser
------------------------ Yahoo! Groups Sponsor --------------------~--> Most
low income households are not online. Help bridge the digital divide today!
http://us.click.yahoo.com/cd_AJB/QnQLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate
folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press
the "search" button.
Yahoo! Groups Links
------------------------ Yahoo! Groups Sponsor --------------------~-->
Get Bzzzy! (real tools to help you find a job). Welcome to the Sweet Life.
http://us.click.yahoo.com/A77XvD/vlQLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/