The only option I can think of for this application is to model two different
types of chillers. Use an air-cooled chiller(s) for the dry case, and a water-
cooled chiller(s) with tower for the evaporative case. I will add this to the
list of suggestions for new features in the future.
The siwitchover can be controlled by load range or by schedule. By reporting
hourly chiller loads and outdoor dry bulb temperatures, you can probably come
up with a suitable load below which the air-cooled chiller should be used. Or
you could take the hourly dry bulb temperatures and create two custom schedules
(one schedules equals 1 at ODB>=6C, the other schedule equals 1 at ODB<6C) in a
csv file and use the SCHEDULE:FILE:COMMA object to read these schedules.
Mike
On 10 Nov 2005, at 8:10, christian1855 wrote:
> Dear all,
> I'd like to simulate a building where the air-conditioning system use
> wet/dry cooling towers. If the ambient temperature is below 6°C the
> nonevaporative air-cooled heat exchanger portion handle the entire
> heat load (similar to the cooling tower as described in ASHRAE,
> Systems and Equipment p36.5, fig 13). I haven't found any according E+
> object.
> Is there an object for modeling a wet/dry cooling tower?
>
> In my case the wet and dry part of the tower did never work at same
> time, therefore it is possible to split the tower in 2 components:
> -) a standard cooling tower (wet)
> -) air-cooled heat exchanger (dry)
> which use the same fan.
> But now the next question araise: How can I model a dry cooling tower?
>
> Christian
>
>
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
Get Bzzzy! (real tools to help you find a job). Welcome to the Sweet Life.
http://us.click.yahoo.com/A77XvD/vlQLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/