[EnergyPlus_Support] Problems with coil:water:cooling in a unit ventilator
Dear all,
currently I'm modelling a server-room with high electric load (up to
700W/m2). For zone cooling I'm using a UnitVentilator. Actually there
are 4 cooling elements in the room.
One element is specified as:
Air-Temperature-in: 24 °C
Air-Temperature-out: 14.2 °C
Air-volumn flow rate: 6.11 m3/s
Water-Temperature-in: 12 °C
Water-Temperature-out:18 °C
Water-volumn flow rate: 0.0029 m3/s
Total cooling power: 73kW
The electric load in the zone is about 130kW. The 4 cooling elements
have a total cooling power of ~292kW which is more then twice the
internal load. So if the unit ventilator works correctly the zone
should be exact on the zone setpoint temperature.
When I use a coil:water:cooling in the unit ventilator and specify the
input values as mentioned above (except the flow-rates have been
multiplied with 4) the zone setpoint temperatures cannot be achieved!
Everything else seems to be OK: no errors, no warnings, correct air
flow rate, correct water flow rate, correct water inlet temperature,.
.. (same result in E+ v1.2.2 and v1.2.3).
I've now manually calculated the UA value for my cooling element,
changed the cooling coil to a coil:water:simplecooling object, used
this UA value (93870 W/K for 4 elements) and the model will give the
expected result.
Are there any know issues using the UnitVentilator with a coil:water:
cooling?
Christian
PS: I will upload the idf file: unitVentilatorCoolingCoilProblem.zip
------------------------ Yahoo! Groups Sponsor --------------------~-->
Fair play? Video games influencing politics. Click and talk back!
http://us.click.yahoo.com/T8sf5C/tzNLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/