Re: [EnergyPlus_Support] Problems with coil:water:cooling in a unit ventilator
There are no known issues with unit ventilator, but there are some unverified
issues with coil:water:cooling. I have asked someone else to look at this
further. If you are in a hurry, you might try using
COIL:Water:DetailedFlatCooling.
Mike
On 11 Nov 2005, at 17:05, christian1855 wrote:
> Dear all,
> currently I'm modelling a server-room with high electric load (up to
> 700W/m2). For zone cooling I'm using a UnitVentilator. Actually there
> are 4 cooling elements in the room.
>
> One element is specified as:
> Air-Temperature-in: 24 °C
> Air-Temperature-out: 14.2 °C
> Air-volumn flow rate: 6.11 m3/s
> Water-Temperature-in: 12 °C
> Water-Temperature-out:18 °C
> Water-volumn flow rate: 0.0029 m3/s
> Total cooling power: 73kW
>
> The electric load in the zone is about 130kW. The 4 cooling elements
> have a total cooling power of ~292kW which is more then twice the
> internal load. So if the unit ventilator works correctly the zone
> should be exact on the zone setpoint temperature.
>
> When I use a coil:water:cooling in the unit ventilator and specify the
> input values as mentioned above (except the flow-rates have been
> multiplied with 4) the zone setpoint temperatures cannot be achieved!
> Everything else seems to be OK: no errors, no warnings, correct air
> flow rate, correct water flow rate, correct water inlet temperature,.
> .. (same result in E+ v1.2.2 and v1.2.3).
>
> I've now manually calculated the UA value for my cooling element,
> changed the cooling coil to a coil:water:simplecooling object, used
> this UA value (93870 W/K for 4 elements) and the model will give the
> expected result.
>
> Are there any know issues using the UnitVentilator with a coil:water:
> cooling?
>
> Christian
>
> PS: I will upload the idf file: unitVentilatorCoolingCoilProblem.zip
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
Get Bzzzy! (real tools to help you find a job). Welcome to the Sweet Life.
http://us.click.yahoo.com/A77XvD/vlQLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/