Re: [EnergyPlus_Support] High Mean Air Temperature in Winter
Dear Mike,
Thank you for the reply.
I could not understand the meaning of:
"the position of the living space is shifted from the other zone
as seen in the dxf output file"
As I do not have the software to view the drawing file,
could you please take a look of the building structure I have uploaded?
What should the value of floor's view factor to ground be?
The value of 0 and 1 both give an error of:
Floor Tilt=0.0, much less than expected tilt of 180, for Surface=FLOOR: LIVING, in Zone=LIVING ZONE
About the high MAT in Winter,
I made a comparison with another simulation software,
with the same building construction and weather data,
the MAT came out in a totally different trend
(comparison graph in the same file)
Although the other simulation programme uses Resistance Network Solution,
I suppose the results would not differ to such an extent..
The file is uploaded as HighMeanAirTemperatureInWinter2
Please advice and thank you!
PuiWah
こんにちは。
In message "Re: [EnergyPlus_Support] High Mean Air Temperature in Winter",
Michael J. Witte wrote...
>My apologies for the delayed response.
>
>The reporting for solar gains is somewhat confusing, because some of the
>variables are W/m2, and some are W.
>
> Environment:Diffuse Solar [W/m2]
> Environment:Direct Solar [W/m2]
> Zone Transmitted Solar[W]
>
>Dividing Zone Transmitted Solar[W] by the total window are of the zone gives
>numbers which are smaller than the sum of environment diffuse and direct.
>
>These results look quite reasonable to me. The south wall is mostly glass with
>overhangs, and the sun is low in January, so the solar gains through the south
>windows in January will actually be greater than in July. This is a small
>zone, and the outdoor temperatures are 0 to 13C, so I would expect the solar
>gains to quickly warm the space during the daytime.
>
>I noticed that the position of the living space is shifted from the other zone
>as seen in the dxf output file. You may want to check the geometry inputs.
>
>Mike
>
>
>On 24 Oct 2005, at 13:40, 黄佩華 wrote:
>
>> Hello.
>>
>> I am trying to model the Living zone of a single storey residential
>> building. It is a 5m(X) x 3.6m(Y) x 3.75m(Z) space, with 6.8m2 South
>> Window and 1.2m2 West Window, without space heat gain, purchased air
>> heating and cooling.
>> Weather data used is JAPAN_Osaka_IWEC.epw.
>>
>> During Winter, the Living Zone MAT gets so high (i.e. 2,4,7,9,10 Jan
>> above 30C; 5,6,8 Jan above 25C) that purchased air heating does not
>> need to function. As the MAT for Summer during period without cooling
>> is around 35C, I wonder how the Winter MAT becomes so high.
>>
>> A rough comparison of Zone Transmitted Solar shows it is at least 2 or
>> 3 times the sum of Direct and Diffuse Solar in Winter, but about the
>> same with sum of Direct and Diffuse Solar in Summer. I could not find
>> the explanation of how Solar Radiation Transmission through Windows is
>> calculated in the Engineering Doc thus just comparing directly though
>> they are of different units.
>>
>> I have uploaded the idf file: HighMeanAirTempInWinter.
>>
>> Please advice.
>>
>> Thank you.
>>
>> Wah
>>
>>
>>
>>
>>
>>
>>
>>
>> The primary EnergyPlus web site is found at:
>> http://www.energyplus.gov
>>
>> The group web site is:
>> http://groups.yahoo.com/group/EnergyPlus_Support/
>>
>> Attachments are not allowed -- please post any files to the appropriate folder
>> in the Files area of the Support Web Site.
>>
>> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
>> "search" button.
>>
>> Yahoo! Groups Links
>>
>>
>>
>>
>>
>>
>>
>>
>
>
>
>========================================================
>Michael J. Witte, GARD Analytics, Inc.
>EnergyPlus Testing and Support
>EnergyPlus-Support@xxxxxxxx
>
>
>
------------------------ Yahoo! Groups Sponsor --------------------~-->
Get Bzzzy! (real tools to help you find a job). Welcome to the Sweet Life.
http://us.click.yahoo.com/A77XvD/vlQLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.