Re: [EnergyPlus_Support] Loads Initialization did not Converge (CheckWarmupConvergence)



Possible causes: 

very high thermal mass such as very thick concrete (solution: increase max 
number of warmup days in the BUILDING object); 

moderate mass and inadequate space conditioning such that the building keeps 
getting warmer and warmer on successive days (solution:  add HVAC, check 
building thermal properties, check if infiltration is included); 

a soil layer modeled below the concrete slab - (solution remove this layer and 
read about ground temperatures in the Auxiliary Programs document).

Mike

On 11 Nov 2005, at 19:05, Studio Tecnico Pentium Associati - Arezzo wrote:

> Dear groupers,
> I'm simulating a simple room, but I always get this warning message:
> 
> Loads Initialization did not Converge (CheckWarmupConvergence)
> 
> What should I check?
> 
> Thank you,
> Enrico
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




------------------------ Yahoo! Groups Sponsor --------------------~--> 
Get Bzzzy! (real tools to help you find a job). Welcome to the Sweet Life.
http://us.click.yahoo.com/A77XvD/vlQLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/