RE: [EnergyPlus_Support] Heat Recovery Unit and Primary Air Loop
It sounds like you need to use one of these objects: 'Coil:DX:CoolingHeatExchangerAssisted' or 'Coil:Water:CoolingHeatExchangerAssisted'.
-----Original Message-----
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]On Behalf Of Clarice Bleil de Souza
Sent: Tuesday, December 13, 2005 6:16 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Heat Recovery Unit and Primary Air Loop
Hi everybody,
I am trying to simulate a Heat Recovery Unit + a Cooling Coil in a Primary Air Loop, which then feeds treated fresh air to a Secondary Air Loop with Fancoil systems.
I had problems connecting this Primary Air Loop to the Outside Air node of the Fancoils, there's probably sth in the code that doesn't allow it to happen as Fancoils are pretty standard machines. So I decided to mix the air in the zones directly.
I built up a Primary Air Loop with a Heat Recovery Unit + a Cooling Coil and I want to deliver treated fresh air directly to each zone using a Direct Air object after the Zone Splitter. The system seems to be working perfectly whenever the Heat Recovery Unit is not connected to it.
Once I plug the Heat Recovery Unit in, the simulation crashes because there are problems in connecting it to the Outside Air Mixer in the Primary Air Loop and also control problems. I couldn't figure out what exactly was wrong with my files, first I thought that it might not be possible to connect a Heat Recovery Unit to an Primary Air Loop then I thought that maybe a template would help me. Does anybody has any template for Heat Recovery Units connected to primary Air Loops?
I thank you in advance for the attention and help
Regards,
Clarice
---------------------------------
Yahoo! doce lar. Faça do Yahoo! sua homepage.
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
_____
YAHOO! GROUPS LINKS
* Visit your group " EnergyPlus_Support <http://groups.yahoo.com/group/EnergyPlus_Support> " on the web.
* To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>
* Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service <http://docs.yahoo.com/info/terms/> .
_____
[Non-text portions of this message have been removed]
------------------------ Yahoo! Groups Sponsor --------------------~-->
Most low income homes are not online. Make a difference this holiday season!
http://us.click.yahoo.com/5UeCyC/BWHMAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/