This error probably means that you have values of 2, 3, or 4 in the Control
Type schedule for this thermostat. For this heating-only system, when heating
is available the control type schedule value should be 1. When heating is not
available, set the control type schedule value to zero.
Mike
On 15 Dec 2005, at 14:07, ogocer@xxxxxxxxxxxxxx wrote:
> Dear All,
> i want to simulate a building which will be only heated during heating
> season and in summer will be cooled only with natural ventilation. i use
> purchased air system and set heating setpoints and schedules. Because in
> summer i don't want to use any system for cooling. So, heating setpoint
> schedule includes only 6 months of the year. Zone controls and termostat
> objects have only single heating setpoint. But at the end of simulation
> error file asks cooling setpoint and schedule. What can i do to simulate a
> purchased air system only for heating?
> thanks
> ozgur gocer
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
Most low income homes are not online. Make a difference this holiday season!
http://us.click.yahoo.com/5UeCyC/BWHMAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/