[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] moisture by other_equipment
I am not sure if this was a new question or not . . .
Use the "Fraction Latent" to specify the rate of moisture addition in Watts.
The heat of vapoization is determined internally every time step as a function
of the current zone temperature and humidity, and it will be approximately
2,500,000 J/kg.
Mike
On 10 Jan 2006 at 7:48, eplus2002mt wrote:
> how can I bring in MOISTURE by these parameters?
> OTHER EQUIPMENT,
> A1 , \field Name
> N1 , \field Design Level
> \units W
> N2 , \field Fraction Latent
> \required-field
> N3 , \field Fraction Radiant
> N4 ; \field Fraction Lost
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/