[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] Disparate zones for inlet and outlet nodes for an air loop
My apologies for the delayed response . . .
There is no easy way to model this case.
The simplest solution is to take the return air from the corridor and forget
about the other flows. If you expect those zones to be at similar
temperatures, this will probably be adequate from an energy use perspective.
Another option would be to combine the corridor/lobby area with the toilet area
into a single zone. A zone can be made up of non-contiguous spaces.
Mike
On 11 Jan 2006 at 18:19, Elmer Morrissey wrote:
> One of the AHUs services a particular loop in one area and takes
> extract from another area. It provides ventilation air to a corridor
> and lobby area. However, the return loop is extracting air from three
> toilet areas. These areas are physically separated within the building
> by 2/3 zones. Is this a problem in EnergyPlus, and do I have to
> conglomerate these disparate areas into one zone (this may be a
> problem with disparate temperature control etc)?
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/