Hi Mike, 

If I conglomerate the areas into one zone, I think I can safely ignore
the degree or two difference in room temperature. However, the AHU
supplies air at a rate of 141l/s and exhausts at a rate of 204l/s (due
to the inflated exhaust rates required for toilet areas). I can't seem
to force this situation? What am I missing? Can I set the extract VAV
to always extract air at a larger rate than the supply air?

Kind regards

-Elmer



--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@g...> wrote:
>
> My apologies for the delayed response . . .
> 
> There is no easy way to model this case.
> 
> The simplest solution is to take the return air from the corridor
and forget 
> about the other flows.  If you expect those zones to be at similar 
> temperatures, this will probably be adequate from an energy use
perspective.
> 
> Another option would be to combine the corridor/lobby area with the
toilet area 
> into a single zone.  A zone can be made up of non-contiguous spaces.
> 
> Mike
> 
> On 11 Jan 2006 at 18:19, Elmer Morrissey wrote:
> 
> > One of the AHUs services a particular loop in one area and takes 
> > extract from another area. It provides ventilation air to a corridor 
> > and lobby area. However, the return loop is extracting air from three 
> > toilet areas. These areas are physically separated within the
building 
> > by 2/3 zones. Is this a problem in EnergyPlus, and do I have to 
> > conglomerate these disparate areas into one zone (this may be a 
> > problem with disparate temperature control etc)?
> 
> 
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support      
> EnergyPlus-Support@g...
>







The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/