Re: [EnergyPlus_Support] Outside convective heat transfer coefficient
If you mean a WINDOWSHADE rather than a shading surface, exterior shades and
blinds convect with the outside air and the airflow in the gap between the
shade or blind and the outside glass layer is also modeled. The gap flow is
affected by temperature differences and by the shade or blind characteristics.
In the case of the shade, the "Air flow permeability" is a factor in this
calculation. My understanding is that the reported convection coefficients are
for the shade or blind convecting to the outside air, not the effective
convection coefficient for the glass layer, but I am not 100% sure of this.
The Engineering Reference discusses shading layer heat balances in detail, see
"Heat Balance Equations for Shading Device and Adjacent Glass", beginning on p.
191, pdf p. 219.
Mike
On 16 Feb 2006 at 5:29, Linda Lawrie wrote:
> At 02:28 AM 2/16/2006, Peter G Loutzenhiser wrote:
> >If I have a an exterior shade mounted over a glazing unit, what is
> >the output for the exterior convective heat transfer coefficient
> >giving me is it the heat transfer coefficient on the outer window
> >surface or the outer shading surface?
>
> Since shading surfaces are NOT heat transfer surfaces, the exterior
> convective coefficent reporting is on outer window surface.
>
>
> Linda
>
> EnergyPlus WebSite: http://www.energyplus.gov
> Owner: EnergyPlus_Support list
> Member: EnergyPlus Development Team
>
>
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/