Sebastian,
Let me see if I got the point of your question correctly. Are you
interested in subdividing a thermal zone into two COMIS airflow zones solely
because you want to see the individual air flows through two windows from
that zone to the outdoors ? If so, I'm afraid you're out of luck The
original COMIS program allows users to print out the air flows through each
node, i.e., window or crack, but these variables are not passed to
EnergyPlus in the current implementation. We also did not foresee the need
for allowing a COMIS zone without a thermal counterpart, from which
EnergyPlus derives the zone volume, neutral height, etc. Therefore, my only
suggestion is for you to also create two thermal zones corresponding to the
COMIS zones, and proceed accordingly. I have no suggestions on how to model
the "interior wall" , either thermally and air-flow-wise, between the two
zones (or subzones).
Joe Huang
(implementer of the EnergyPlus/COMIS link 2000-2001)
----- Original Message -----
From: "sebastian.coene" <sebasje27@xxxxxxxxx>
To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Monday, February 20, 2006 12:24 PM
Subject: [EnergyPlus_Support] COMIS + nodes
> hi,
>
> My question:
>
> I have a 1 zone model and use comis for natural ventilation. Now, i
> want to know mass flow through two openings on oppostite sides of the
> zone.
> I must define 2 external nodes at each of the two windows through wich
> the air flows.
>
> BUT can i define a node in the middle of the zone for use only in
> COMIS? I can't find it in the manual? Only thing i can find is the
> defining of nodes for all types of mechanical ventilation.
> Or do i use 'Air mass flow from fromzone to tozone' for this?
>
> Any one knows the answer? Or how to define internal nodes for use in
> COMIS?
>
> Thanks in advance,
> Sebastian
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate
> folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press
> the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/