[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: Combiining systems to manage zone temperature
Hi Mike,
As I said before, i seperated the system from the building in order
to speed up analysis in order to debug it. In this test file, I am
getting the two working simultaneously however they do not achieve
the 16C setpoint set for the zone during the winter months? The temp
in the zone seems to come close but never achieve the setpoint. Can
you spot what is going on?
I've uploaded the file? it's in the problem submittals and its
called SF01Baseboard.idf
I am using an Irish weather file and the UA I've set for the
baseboard and the coil should have raised zone temperature
sufficiently?!
Kind regards and thanks in advance
-Elmer
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@...> wrote:
>
> That should work. Please upload the input file to the yahoo group
files area
> or send (zipped) to energyplus-support@...
>
> Mike
>
> On 28 Feb 2006 at 17:21, Elmer Morrissey wrote:
>
> > Hi all,
> >
> > I am having a problem with a system that takes fresh air (which
is
> > heated by a heating coil) and baseboard heaters to keep a zone
at a
> > particular temperature.
> >
> > It looks like
> >
> > ZONE EQUIPMENT LIST,
> > zGrdPrivateDining Equipment,
> > DIRECT AIR,
> > zGrdPrivateDining Dir Air,
> > 1,
> > 1,
> > BASEBOARD HEATER:Water:Convective,
> > zGrdPrivateDining TH,
> > 2,
> > 2;
> >
> > Unfortunately, despite the fact that my zonal temperaturess are
> > never getting near the 20C setpoint, the baseboard heater and
air
> > system are never combining to increase the zone temp.
> >
> > The reason I am so confused is because the baseboard heaters in
> > other rooms are working fine when the are the only equipment
> > managing room temperatures.
> >
> > Kind regards
> >
> > -Elmer
> >
> >
> >
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
appropriate folder
> > in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf
and press the
> > "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
> >
> >
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@...
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/