Re: [EnergyPlus_Support] Problem with Max Heating Rate Values



Max values in table reports are computed for each timestep.  My guess is that 
the report variables are being reported hourly, so you are only getting the 
maximum rate averaged over one hour in that view.  Set the REPORT VARIABLE 
reporting frequency to TIMESTEP (for Zone timestep variables) or DETAILED (for 
HVAC timestep variables), and the max values should match what is reported in 
the table report.

Mike

On 2 Mar 2006 at 19:42, pacmon2004 wrote:

> Hello,
>  I have noticed that maximum heating rate values obtained with 
> Report:Table:Monthly are very different(much larger)than the ones that 
> can be obtained from the report of heating rates in Report Variable. 
> This happens when using Purchased Heating aa well as with a Heat Pump 
> System. Am I overlooking something or doing something wrong ?
> 
> Thanks for any clarification. 
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
>  
> Yahoo! Groups Links
> 
> 
> 
>  
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/