Re: [EnergyPlus_Support] attached shading surface with some holes



"Fraction of Shading Surface That Is Glazed" in Shading Surface Reflectance 
only affects the way the shading surface *reflects* sunlight, it does not alter 
the transmittance of the shading surface.

Shading surfaces are opaque, unless the the transmittance schedule (field 
"TransSchedShadowSurf") has values greater than 0.0.  The easiest option is to 
set the shading surface transmittance schedule to AreaOfHoles divided by 
TotalAreaOfShade.

Mike


On 9 Mar 2006 at 9:56, dademarino wrote:

> Dear Users of EnergyPlus,
> 
> I have an attached shading surface with some holes.
> How  can describe these holes geometrically? 
> Can I use field "fraction of shading surface that is glazed" in shading 
> surface reflectance object without describe geometrically these holes?
> In this way in order to model these holes I use a window glass with 
> very high transmittance and very low reflectance.
> Is this correct?
> 
> Best Regards,
> 
> Marino Davide.
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
>  
> Yahoo! Groups Links
> 
> 
> 
>  
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/