Reference ExampleFiles\RadLoHydrHeatCoolAuto.idf. The objects required to
defined a low temp radiant floor are:
CONSTRUCTION WITH INTERNAL SOURCE
LOW TEMP RADIANT SYSTEM:HYDRONIC
plus the usual zone control objects required for any HVAC systems (ZONE
CONTROL:THERMOSTATIC, CONTROLLED ZONE EQUIP CONFIGURATION, ZONE EQUIPMENT LIST)
and plant loops and branches to connect it to the boiler.
LOW TEMP RADIANT SYSTEM:HYDRONIC requires specification of the "Hydronic tubing
inside diameter" and the tubing length and water flow rate can be autosized.
Mike
On 20 Mar 2006 at 20:59, sebastian.coene wrote:
> hi, a second question for today
>
> What is the way to implement underfloor heating in a simple way? I
> thought about using a low temp radiant system? If this is a good
> choice, do I need to make another object because I don't see a link
> with any other objects? (except for the nodes offcourse)
>
>
> greets,
> Sebastian
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/