No problem. Thanks for confirming that the values are consistent. Mike
On 20 Apr 2006 at 18:02, Clarice Bleil de Souza wrote:
> Dear Mike
>
> Thanks a lot for the reply.
> I recalculate the conductance without the film coefficients and the values
> do match. E+ is reporting the conductance of the composition in the eio file
> and I thought it was reporting the U-value. The film coeff you are using are
> almost the same I used - 0.12 Rsi and 0.03 Rso. So everything matches - I just
> didn't realise that E+ was ploting the conductance instead of the U-value. My
> fault - sorry for that :(
>
> Thanks a lot for the reply
>
> Regards,
>
> Clarice
>
> "Michael J. Witte" <mjwitte@xxxxxxxx> escreveu:
> As you know, the surface details report (report, surfaces, details;) gives
> U-
> values with and without film coefficients. The construction report (report,
> construction;) reports a thermal conductance without film coefficients, which
> should be the same value as the "Nominal U (w/o film coefs)".
>
> For the "Nominal U (with film coefs)", there is a table of film coefficients
> given in the "Output Details and Examples" document, p. 26 (pdf p. 32). I see
> that this table is in I-P units. Here are the values in S-I units (which we
> will add to the document, but it might be too late to add for the 1.3
> release).
> These values are directly from the source code:
>
> Surface type, Interior film, Exterior film {m2-K/W}
>
> Wall, 0.1197548 , 0.0299387
>
> Floor, 0.1620212 , 0.0810106
>
> Ceiling/Roof, 0.1074271 , 0.0810106
>
>
> Would you please repeat your hand calculations using the above values and
> confirm if this agrees with the reported "Nominal U (with film coefs)"?
>
> Mike
>
>
>
> On 20 Apr 2006 at 13:03, Clarice Bleil de Souza wrote:
>
> > Hi Everybody,
> >
> > I am trying to run some simulations with different U-values to check the
> > sensitivity of the results and I was wondering, how does E+ calculates the
> > U-values.
> > I have some material compositions that gives me 0.5w/m2K calculated by
> hand
> > (using Rso = 0.055 and Rsi = 0.123 - using the inverse sum of the
> > resistivities in series) and E+ gives me 0.55 which is near. Once I look for
> a
> > more conductive material with a hand calculated value of 3 w/m2K, Energy
> Plus
> > gives me a value of 6.5W/m2K. I could not understand why this is happenning.
> I
> > know the U-values won't be used by E+ but I want to be sure that results
> will
> > be somehow equivalent. Can you please let me know how E+ calculates the
> > U-values? I couldn't find anything about it in the documentation.
> >
> > Thanks a lot for your attention and hope hearing from you soon,
> >
> > Regards,
> >
> > Clarice
> >
> >
> >
> >
> > ---------------------------------
> > Abra sua conta no Yahoo! Mail - 1GB de espaço, alertas de e-mail no celular
> e
> > anti-spam realmente eficaz.
> >
> > [Non-text portions of this message have been removed]
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the appropriate
> folder
> > in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press
> the
> > "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
> >
> >
> >
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@xxxxxxxx
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
>
>
>
> ---------------------------------
> YAHOO! GROUPS LINKS
>
>
> Visit your group "EnergyPlus_Support" on the web.
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.
>
>
> ---------------------------------
>
>
>
>
>
> ---------------------------------
> Abra sua conta no Yahoo! Mail - 1GB de espaço, alertas de e-mail no celular e
> anti-spam realmente eficaz.
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/