While EnergyPlus supports glycol solutions, not all components support it.
EnergyPlus will allow "water" loops to go below zero C without freezing the
loop. You do not need two separate loops.
Mike
On 10 May 2006 at 14:21, jingjuan_feng wrote:
> Hi,
> I am now trying to simulate an ice thermal storage system with
> EnergyPlus, and I have studied the 5zoneicestorage and
> Detailedicestorage example file as reference. In this file, in the
> charging mode, the chilled water setpoint is set to be -5. However, at
> this tempreture the water is already frozen. Usually, this tempreture
> is given to glycol or brine. What's more, in the <Input and Output
> reference> and <Engineering Reference>, I can not clearly find out the
> loop for glycol. Since it has suggestted that the ice storage tank
> should be placed in the chilled water supply side outlet branch, and
> must be followed by a pipe component in series, I have some
> difficulties in adding purchased cooling in cw supply loop,because
> the supply side have two type of fluid: one is water and another is
> glycol that only one bypass branch is not proper.
> I am now in urgent need for the answer. Thank you very much!
>
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
Protect your PC from spy ware with award winning anti spy technology. It's free.
http://us.click.yahoo.com/97bhrC/LGxNAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/