[EnergyPlus_Support] outside air load



Dear,
   I created a model with purchased air and determined to introduce 
OA as infiltration or ventilation .There is an independent oustside 
air unit in my real hvac system,so i want to gain oa load to select 
appropriate oa unit.I encounter some problems as follows:

  1.When i introduce oa as infiltration ,according to former 
suggestion,i can gain oa load by compare the values between the model 
has infiltration(oa) and the model has not.But i'm puzzled at this 
method.In real oa unit,the outside air has been cooled to 14¡æ in 
summer and heated to 50¡æ in winter.The oa unit and air condition 
system worked together to cool or heat the zone.But when i introduce 
oa as infiltration ,it seemed to that the outside air is just been 
conditioned to zone air temp by air condition system(25¡æ in summer 
and 22¡æin winter).Although  the total load did't change,distinctly 
the gained oa load is smaller if i used this comparative method to 
gain oa load.Then how can i gain the real oa load?

  2.I want to introduce oa as ventilation.I don't know how to set he 
minimum indoor temp in ventilation.Because the temp is different in 
summer and winter.How to set the ventilation variables?

   Thanks very much! 
   pch






------------------------ Yahoo! Groups Sponsor --------------------~--> 
You can search right from your browser? It's easy and it's free.  See how.
http://us.click.yahoo.com/_7bhrC/NGxNAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/