Thank you for the response,Mike. It sounds like my description of
OAFractionSched misled you. In fact, I have to get preliminary sizes
when I start to simulate a A/C system. The real air conditoning unit
is however an oversized one than the E+ suggest --it can supply
overmuch cooling amount than needs. Users have to adjuge the FA
damper to force normal outdoor air intake. In this simulation, I
use the real FA flow rate (about same with the autosize value) , and
the real cooling capactiy(larger than the autosize value).
The "flowrate/capacity" will be out of range. How can I simulate
this case?
Or I can describe it like this: I simulate an AC unit and get good
autosize values about the unit. Then given that I want to know what
it will look like to change to an oversized equipment, by keep
preliminary size of OA and enlarge the nominal cooling supply two
times --this situation I guess could happen in reality.
I hope this time I explain the question clearer. THank you in
advance.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@...> wrote:
>
> My apologies for the delayed response.
>
> I am not sure I understand completely what you are trying to do.
When
> economizer operation is not active, the outside air flow rate is
calculated as
> follows. All names in quotes are field names for
CONTROLLER:OUTSIDE AIR:
>
> a) If "MinimumLimit"=FIXED MINIMUM, then OAFlowRate = "minimum
outside air flow
> rate" * "Minimum Outside Air Schedule"
>
> b) If "MinimumLimit"=PROPORTIONAL MINIMUM, then OAFlowRate
= "minimum outside
> air flow rate" * "Minimum Outside Air Schedule" * (Current system
flow
> rate/Design system flow rate)
>
> It sound like you need to specify a value for "minimum outside air
flow rate".
> If you autosize this, the autosize value is the sum of the outside
air
> requirements in the ZONE SIZING objects for zones served by this
air loop.
>
> Does this give you enough information to control the outside air
flow as
> desired?
>
> On 7 May 2006 at 4:12, eric_zhou1223 wrote:
>
> > Hi all,
> >
> > I was trying to simulate an oversized equipment in a real
> > project. A huge amount of outside air was introduced in the
> > simulation, because I must manually size both the capacity and
flow
> > rate at the same time and increase them proportionally to avoid
the
> > out of range error.
> >
> > To keep appropriate outdoor air intake, I have to remain the
> > autosizing value of airflow rate while only to increase the
> > autosized capacity to the real value by some way.
> >
> > I noticed there is a OAFractionSched in Controller:outside Air
which
> > now is all set to 1. Can I change it to a small number (such as
> > 0.01) to consider a situation where an oversized equipment is
used
> > like in my case? Is it the key to solve an oversized unit's
> > simulation? I found modifying OAFractionSched as 0.01 didnot
lead
> > to an expected result like "OA =0.01* original air flowrate" .
> > Instead,it was a much smaller value seemingly no related to the
> > original one.
> >
> > Could anybody instruct me how to simulate an oversized equipment
> > like this? Thank you.
> >
> > Eric
> >
> >
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
appropriate folder
> > in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf
and press the
> > "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
> >
> >
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@...
>
------------------------ Yahoo! Groups Sponsor --------------------~-->
You can search right from your browser? It's easy and it's free. See how.
http://us.click.yahoo.com/_7bhrC/NGxNAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.