[EnergyPlus_Support] Re: Oversized equipment




Thank you for the response,Mike. It sounds like my description of 
OAFractionSched misled you. In fact, I have to get preliminary sizes 
when I start to simulate a A/C system. The real air conditoning unit 
is however an oversized one than the E+ suggest --it can supply 
overmuch cooling amount than needs. Users have to adjuge the FA 
damper to force normal outdoor air intake.  In this simulation, I 
use the real FA flow rate (about same with the autosize value) , and 
the real cooling capactiy(larger than the autosize value).  
The "flowrate/capacity" will be out of range.  How can I simulate 
this case?

Or I can describe it like this:  I simulate an AC unit and get good 
autosize values about the unit. Then given that I want to know what 
it will look like to change to an oversized equipment, by keep 
preliminary size of OA and enlarge the nominal cooling supply two 
times --this situation I guess could happen in reality.
I hope this time I explain the question clearer. THank you in 
advance.


--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte" 
<mjwitte@...> wrote:
>
> My apologies for the delayed response.
> 
> I am not sure I understand completely what you are trying to do.  
When 
> economizer operation is not active, the outside air flow rate is 
calculated as 
> follows.  All names in quotes are field names for 
CONTROLLER:OUTSIDE AIR:
> 
> a) If "MinimumLimit"=FIXED MINIMUM, then OAFlowRate = "minimum 
outside air flow 
> rate" * "Minimum Outside Air Schedule"
> 
> b) If "MinimumLimit"=PROPORTIONAL MINIMUM, then OAFlowRate 
= "minimum outside 
> air flow rate" * "Minimum Outside Air Schedule" * (Current system 
flow 
> rate/Design system flow rate) 
> 
> It sound like you need to specify a value for "minimum outside air 
flow rate".  
> If you autosize this, the autosize value is the sum of the outside 
air 
> requirements in the ZONE SIZING objects for zones served by this 
air loop.
> 
> Does this give you enough information to control the outside air 
flow as 
> desired?
> 
> On 7 May 2006 at 4:12, eric_zhou1223 wrote:
> 
> >   Hi all,
> > 
> >  I was trying to simulate  an oversized equipment in a real 
> > project.  A huge amount of outside air was introduced in the 
> > simulation, because I must manually size both the capacity and 
flow 
> > rate at the same time and increase them proportionally to avoid 
the 
> > out of range error.
> > 
> > To keep appropriate outdoor air intake,  I have to remain the 
> > autosizing value of airflow rate while only to increase the 
> > autosized capacity to the real value by some way.
> > 
> > I noticed there is a OAFractionSched in Controller:outside Air 
which 
> > now is all set to 1. Can I change it to a small number (such as 
> > 0.01) to consider a situation where an oversized equipment is 
used 
> > like in my case?   Is it the key to solve an oversized unit's 
> > simulation?  I found modifying OAFractionSched as 0.01 didnot 
lead 
> > to an expected result like "OA =0.01* original air flowrate" . 
> > Instead,it was a much smaller value seemingly no related to the 
> > original one.
> >  
> > Could anybody instruct me how to simulate an oversized equipment 
> > like this? Thank you.
> > 
> > Eric
> > 
> > 
> > 
> > 
> > 
> > 
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> > 
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> > 
> > Attachments are not allowed -- please post any files to the 
appropriate folder
> > in the Files area of the Support Web Site.
> > 
> > EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf 
and press the
> > "search" button.
> >  
> > Yahoo! Groups Links
> > 
> > 
> > 
> >  
> > 
> > 
> > 
> > 
> 
> 
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support      
> EnergyPlus-Support@...
>







------------------------ Yahoo! Groups Sponsor --------------------~--> 
You can search right from your browser? It's easy and it's free.  See how.
http://us.click.yahoo.com/_7bhrC/NGxNAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/