1. In a full HVAC system, outside air replaces return air. So the outside air
load is only that required to bring the outside air to room temperature. Any
heating or cooing beyond that point is the same whether the air originated from
the zone or from outside. Also, remember that during cool weather, outside air
can be a benefit, providing free cooling.
2. For VENTILATION to operate at any temperature condition set "Minimum Indoor
Temperature" and "Delta Temperature" to -99C. Confirm this by reporting the
ventilation flow rates on an hourly basis for summer and winter design days.
Mike
On 15 May 2006 at 6:45, hbn_pch wrote:
> Dear,
> I created a model with purchased air and determined to introduce
> OA as infiltration or ventilation .There is an independent oustside
> air unit in my real hvac system,so i want to gain oa load to select
> appropriate oa unit.I encounter some problems as follows:
>
> 1.When i introduce oa as infiltration ,according to former
> suggestion,i can gain oa load by compare the values between the model
> has infiltration(oa) and the model has not.But i'm puzzled at this
> method.In real oa unit,the outside air has been cooled to 14¡æ in
> summer and heated to 50¡æ in winter.The oa unit and air condition
> system worked together to cool or heat the zone.But when i introduce
> oa as infiltration ,it seemed to that the outside air is just been
> conditioned to zone air temp by air condition system(25¡æ in summer
> and 22¡æin winter).Although the total load did't change,distinctly
> the gained oa load is smaller if i used this comparative method to
> gain oa load.Then how can i gain the real oa load?
>
> 2.I want to introduce oa as ventilation.I don't know how to set he
> minimum indoor temp in ventilation.Because the temp is different in
> summer and winter.How to set the ventilation variables?
>
> Thanks very much!
> pch
>
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
Home is just a click away. Make Yahoo! your home page now.
http://us.click.yahoo.com/DHchtC/3FxNAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/