Re: [EnergyPlus_Support] Re: Autosizing full FA with heat recovery
Elmer - it is my impression that one can size an air system (and subsequent
plant) for 100% outside air by choosing "Cooling 100% Outside Air" to
be yes
in System Sizing (and maybe also "Healing 100% Outside Air" yes). Can one
have the autosizing take into account heat recovery? No. That is on the
to do list.
Fred Buhl
Elmer Morrissey wrote:
>Hi Mike,
>
>Thank you for the response. I am trying to autosize the OA air
>flowrate but I want full FA (I can't recirc the air due to
>pollutants). As a result, I want to size the full system, so I want
>to autosize the full plant so that it can deal will tempering 100%
>FA conditions. So I guess, I am trying to autosize everything on the
>air and water loop. Should this pose problems?
>
>From what you are saying, if you are trying to autosize absolutely
>everything , you can't force full FA through the air loop (when you
>have a heat recovery unit). Am I right in saying this?
>
>Kind regards
>
>-Elmer
>
>
>
>--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
><mjwitte@...> wrote:
>
>
>>Sorry about the slow response. I do not understand the question.
>>
>>
>What are you
>
>
>>trying to autoszie - the coils or the OA flow rate? It may not be
>>
>>
>possible to
>
>
>>do this with autosizing. You may have to get preliminary sizes
>>
>>
>and force some
>
>
>>flow rates or capacities once you know the main system flow rate.
>>
>>
>Perhaps with
>
>
>>more details or an input file, we can determine how to help.
>>
>>Mike
>>
>>
>>On 8 May 2006 at 23:22, Elmer Morrissey wrote:
>>
>>
>>
>>>Hello all,
>>>
>>>How can you autosize full fresh air when you have a heat recovery
>>>system in an AHU.
>>>
>>>The system is a Heat recovery -> Mixer -> fan -> heating coil ->
>>>
>>>
>zone
>
>
>>>-> return
>>>
>>>In the past, I used an enconmizer to dummy up full FA control
>>>throughout the year. However, I have to set the controller to
>>>
>>>
>BYPASS
>
>
>>>in the Controller: OUTISIDE AIR which makes the old way
>>>
>>>
>impossible to
>
>
>>>implement.
>>>
>>>Can anyone point me in the right direction?
>>>
>>>Kind regards
>>>
>>>-Elmer
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>The primary EnergyPlus web site is found at:
>>>http://www.energyplus.gov
>>>
>>>The group web site is:
>>>http://groups.yahoo.com/group/EnergyPlus_Support/
>>>
>>>Attachments are not allowed -- please post any files to the
>>>
>>>
>appropriate folder
>
>
>>>in the Files area of the Support Web Site.
>>>
>>>EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf
>>>
>>>
>and press the
>
>
>>>"search" button.
>>>
>>>Yahoo! Groups Links
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>========================================================
>>Michael J. Witte, GARD Analytics, Inc.
>>EnergyPlus Testing and Support
>>EnergyPlus-Support@...
>>
>>
>>
>
>
>
>
>
>
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
>EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
>
>Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
[Non-text portions of this message have been removed]
------------------------ Yahoo! Groups Sponsor --------------------~-->
You can search right from your browser? It's easy and it's free. See how.
http://us.click.yahoo.com/_7bhrC/NGxNAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/