With the objective to control minimum relative humidity in a zone, I
have added the following to an air handling system generated using
COMPACT HVAC objects THERMOSTAT, ZONE:UNITARY, and SYSTEM:UNITARY.
a) Humidistat controlling RH in Zone 1 according to a specified RH
schedule.
b) Humidifier located downstream of the AHU "Cooling Coil" and
upstream of the "Zone Splitter". The inlet and outlet nodes of the
humidifier are "Air Loop Outlet" and "Supply Path Inlet". Both of
these nodes were generated using the COMPACT:HVAC objects.
c)A "Setpoint Manager: Single Zone Min Hum" object with "AHU 1
Supply Path Inlet" as the SetPoint Node and "ZONE 1 ZONE AIR NODE"
as the name of the Control Zone Node. Note that the latter field is
called "Name of a Node list (or Node)" in the IDF, while the I/O
Reference describes it as the "name of the zone node of the humidity
control zone". My input was based on the description provided in the
I/O reference (Please confirm whether or not the latest I/O refrence
is accurate on this).
The above modifications made no difference in the results. The
minimum RH specified in the humidistat RH schedule has not been met.
Inspection of the "eplusout.bnd" indicates that there is no
humidifier in the system.
1) Is it possible to add a component such as a humidifier to an air
system created using COMPACT:HVAC objects?
2) How is the signal from the Humidistat used by the "Setpoint
Manager" or the "Humidifier"? I do not see a call/reference to the
humidistat from either of these objects.
3)Do I need to add other objects besides those descibed above to
simulate minimum humidity control?
Please provide insight when you have a chance. Thank you for your
valuable time. Will be happy to upload the model, if needed.
Merid
------------------------ Yahoo! Groups Sponsor --------------------~-->
Everything you need is one click away. Make Yahoo! your home page now.
http://us.click.yahoo.com/AHchtC/4FxNAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/