Re: [EnergyPlus_Support] maximum supply air temperature



Friedl: that is an excellent question. EnergyPlus does not control the 
reheat coils to
an exit air temperature - the coils are controlled to meet the load, and 
the temperature is
whatever results. This isn't a particularly good situation, but it is 
the way things are done now.
You could mitigate your situation by decreasing the max hot water 
flowrate, or lowering the
hot water supply temperature, or increasing the minimum air flow rate.

Fred Buhl

friedl decock wrote:

>Hi,
>
>I'm trying to simulate a VAV-system but I'm not able to control the maximum
>air supply temperature in the zone.
>In the winter the supply air temperature exceeds sometimes 40 degrees while
>the air flow rate is always the minimum value that is allowed.
>
>Does anyone know how to control the max temperature of the supply air in a
>zone (after the reheat coil).
>
>Friedl
>
>
>[Non-text portions of this message have been removed]
>
>
>
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
>EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
> 
>Yahoo! Groups Links
>
>
>
> 
>
>
>
>  
>


------------------------ Yahoo! Groups Sponsor --------------------~--> 
Get to your groups with one click. Know instantly when new email arrives
http://us.click.yahoo.com/.7bhrC/MGxNAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/