Re: [EnergyPlus_Support] SimHVAC - max iterations exceeded -- error
It could be air-side, water-side, controls, overloading, a wide variety of
issues. You mention that the errors are occuring at certain hours of the day.
What type of system are you modeling? Are the errors occuring during recovery
from setback? Or at peak load conditions? Are the zone temperatures being
maintained during these hours? If this is a system with hot water and chilled
water loops, are the loop setpoints being maintained during these hours?
Mike
On 18 May 2006 at 18:19, Dan Karnes wrote:
> Hey all,
>
> I am still learning daily about E+ and am in need of a little expert
> advice. During certain days of simulation, I am getting a varying
> number of errors regarding the max iterations. The error occurs for
> particular hours of the simulation day.
>
> When trying to troubleshoot this error, can I limit my search to the
> air side components only? I am not sure if there is something wrong
> with the model or if it is a weather file problem.
>
> Any advice/experience anyone has to offer would be greatly appreciated.
>
> Thanks.
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
Home is just a click away. Make Yahoo! your home page now.
http://us.click.yahoo.com/DHchtC/3FxNAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/