Re: [EnergyPlus_Support] SimHVAC - max iterations exceeded -- error





"Michael J. Witte" <mjwitte@xxxxxxxx> wrote:    It could be air-side, water-side, controls, overloading, a wide variety of 
issues.  You mention that the errors are occuring at certain hours of the day.  
What type of system are you modeling?
   
  Water cooled VAV system nothing special with respect to (WRT) heat recovery etc.
   
  Are the errors occuring during recovery 
from setback?  Or at peak load conditions?
   
  The errors are mostly occuring just after a night setback time period but some errors are found during peak loading if the modeling day is set to peak.    
   
  Are the zone temperatures being 
maintained during these hours?
   
  I have not found any obvious times when the set-points are not maintained within a small degree that would correlate to the hours the errors are occuring.
   
  If this is a system with hot water and chilled 
water loops, are the loop setpoints being maintained during these hours?
   
  The loop set-points are being maintained during the hours of error.
   
  

Mike

   
   
  I am now in the process of reselecting equipment based on reasonable assumptions to make sure that something isn't under sized.  We had originally had some challenges with a chilled water bypass loop that is not currently being used in the model.  The flow in the bypass loop should have always been zero based on the schedule but sometimes showed some very small flows.  I would like to be sure this is not the error but am not overly confident that I can delete the loop without causing more errors to occur.
   
  Is there any reasonable degree of certainty of how "wrong/inconsistent" the resulting airflows will be while the max simulation error is occuring?  I am assuming given my level of experience that the max sim error is telling me that the trial and error solution of the load calc is not consistent after the warm up days have completed.
   
  Thanks for your help,
   
  Dan
  

 
   
   
   
   
  On 18 May 2006 at 18:19, Dan Karnes wrote:

> Hey all,
> 
> I am still learning daily about E+ and am in need of a little expert 
> advice.  During certain days of simulation, I am getting a varying 
> number of errors regarding the max iterations.  The error occurs for 
> particular hours of the simulation day.  
> 
> When trying to troubleshoot this error, can I limit my search to the 
> air side components only?  I am not sure if there is something wrong 
> with the model or if it is a weather file problem.   
> 
> Any advice/experience anyone has to offer would be greatly appreciated.
> 
> Thanks.
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
>  
> Yahoo! Groups Links
> 
> 
> 
>  
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.





  SPONSORED LINKS 
        Wedding program software   Backup software program   Cad software program     Email software program   Medical software program   Anti virus software program 
    
---------------------------------
  YAHOO! GROUPS LINKS 

    
    Visit your group "EnergyPlus_Support" on the web.
    
    To unsubscribe from this group, send an email to:
 EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
    
    Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service. 

    
---------------------------------
  



		
---------------------------------
Talk is cheap. Use Yahoo! Messenger to make PC-to-Phone calls.  Great rates starting at 1&cent;/min.

[Non-text portions of this message have been removed]



------------------------ Yahoo! Groups Sponsor --------------------~--> 
Get to your groups with one click. Know instantly when new email arrives
http://us.click.yahoo.com/.7bhrC/MGxNAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/