Re: [EnergyPlus_Support] Heat exchanger
Tony,
Is the heat exchanger scheduled to be "available"?
Are you using the bypass feature which is tied to the air-side
economizer? (CONTROLLER:OUTSIDE AIR, field EconomizerChoice= bypass)
These errors won't be shown if the heat exchanger isn't available for a
timestep (via availability schedule) or if its air is being bypassed
because the air-side economizer is operating.
Yes.. the warnings would be in the .err file.
If this doesn't help resolve the issue, then upload your file to the
support web site and we'll take a look.
tonybaxterhevacomp wrote:
>
> Hello anyone,
>
> I am using a HEAT EXCHANGER:AIR TO AIR:GENERIC, my question relates to
> the 'Nominal Supply Air Flow rate'. The manual states that actual flow
> rates should be within 50% to 130% of this or a warning will be given.
> I have tried various values (eg 0.9, 9) with an air lfow rate of 0.3,
> but get no warning, which I assume would be on the .err file. Does
> this field matter - I assume that part load effectiveness uses this
> field, but I am using a constant efficiency independent of low rate.
>
> Many thanks
>
> Tony Baxter
>
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and
> press the "search" button.
[Non-text portions of this message have been removed]
------------------------ Yahoo! Groups Sponsor --------------------~-->
Get to your groups with one click. Know instantly when new email arrives
http://us.click.yahoo.com/.7bhrC/MGxNAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/