See the Input Output reference for the DX cooling coil object. The model
requires that the airflow across the coil remain within a valid range during
the simulation. Check to see that the heatpump object and the coil object are
both set to the same fan mode (cycling or continuous).
Mike
On 10 Jun 2006 at 14:21, Huafen Hu wrote:
> Hello all,
>
> I just got the following warning message when I tried to simulate a
> 800sq.ft residential house. The HVAC system is an air-to-air heat pump and I
> modeled it in E+ using UNITARYSYSTEM:HEATPUMP:AIRTOAIR. Does anybody know
> what's the matter with that? Right now I used a ON/OFF pump but I did try to
> change it to constant volumn pump and the warning keeps.
>
> ** Warning ** COIL:DX:COOLINGBYPASSFACTOREMPIRICAL "HEAT PUMP ACDXCOIL 1" -
> Air volume flow rate per watt of rated total cooling capacity is out of range
> error continues...
>
> Thanks,
> Huafen
>
> __________________________________________________
> Do You Yahoo!?
> Tired of spam? Yahoo! Mail has the best spam protection around
> http://mail.yahoo.com
>
> [Non-text portions of this message have been removed]
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
Check out the new improvements in Yahoo! Groups email.
http://us.click.yahoo.com/6pRQfA/fOaOAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/