Dear Michael
about that question we discuss before, there is another problem. That is how
to define the type of inter-zone walls and window. Are they belong to
exterior wall , and should they be set to sun exposed and wind exposed. If a
internal wall can be set to sun exposed and wind exposed? Thank you .
On 6/22/06, Michael J. Witte <mjwitte@xxxxxxxx> wrote:
>
> Sorry I somehow repeated the question instead of sending an answer. Let's
> try
> this again . . .
>
> 1. Zones do not necessarily require a complet enclosure. If you want
> sunlight
> and heat to be transferred between the atrium zone and the office zones,
> then
> you will need inter-zone walls and windows to model that transfer. Yes,
> the
> inter-zone walls and windows are each described twice, once for each zone,
> facing in opposite directions. It is critical to get the facing
> directions
> correct, or the window will not see sunlight.
>
> 2. I have no advice to offer here. Perhaps someone else does.
>
> Mike
>
>
> On 21 Jun 2006 at 22:46, Michael J. Witte wrote:
>
> > I am simulating a building with a huge glass-roofed atrium. On the two
> > opposite sides of the atrium is floors for offices. Obviously I have to
> > model the office and atrium zones which are adjacent to each other.
> >
> > . . .
> >
> > On 21 Jun 2006 at 18:54, nicole chen wrote:
> >
> > > Dear all,
> > >
> > > I am simulating a building with a huge glass-roofed atrium. On the two
> > > opposite sides of the atrium is floors for offices. Obviously I have
> to
> > > model the office and atrium zones which are adjacent to each other.
> > >
> > > My first questions is whether or not I have to define the inter-zone
> wall
> > > and its associated windows twice for two adjacent zones in EnergyPlus.
> If
> > my
> > > understanding is correct, in E+ each zone needs to be defined with a
> > > complete set of surfaces (say, 6) surrounding it.
> > >
> > > My second question is if there is any modeling tools other than CFD
> that
> > are
> > > capable of simulating the temperature stratefication effect of
> theatrium,
> > > which is approx. 50 meter high.
> > >
> > >
> > > I highly appreciate your help.
> > >
> > > --
> > > Yours
> > > Nicole Chen
> > >
> > >
> > > [Non-text portions of this message have been removed]
> > >
> > >
> > >
> > >
> > > The primary EnergyPlus web site is found at:
> > > http://www.energyplus.gov
> > >
> > > The group web site is:
> > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > >
> > > Attachments are not allowed -- please post any files to the
> appropriate
> > folder
> > > in the Files area of the Support Web Site.
> > >
> > > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and
> press
> > the
> > > "search" button.
> > >
> > > Yahoo! Groups Links
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> >
> >
> > ========================================================
> > Michael J. Witte, GARD Analytics, Inc.
> > EnergyPlus Testing and Support
> > EnergyPlus-Support@xxxxxxxx
> >
> >
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the appropriate
> folder
> > in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and
> press the
> > "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
> >
> >
> >
>
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate
> folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press
> the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
--
Yours
Nicole Chen
[Non-text portions of this message have been removed]
------------------------ Yahoo! Groups Sponsor --------------------~-->
Check out the new improvements in Yahoo! Groups email.
http://us.click.yahoo.com/6pRQfA/fOaOAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/