[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] query
How is the RUN CONTROL object specified in your input file?
If you have "Do the design day simulations" = YES, and "Do the weather
file simulation" = NO, then the weather file is not being used.... only
the design day information/objects in the IDF would be used in that case.
kir kumar wrote:
>Dear mike,
> I have a question.
>I have observed some thing peculiar in Energy plus simulations
>I ran several simulations , each time with same input file(purchased air tables) but different weather files(weather files that come with Energy plus installation).
>I observed that the outdoor dry bulb temperatures in main output spread sheet file in each case. Surprisingly the outdoor dry bulb temperatures of design days are same in each case(each simulation run), no matter what the weather file
>is. Why the outdoor dry bulb temperatures of design days are the same even if I keep changing the weather file.
> thanks
> kiran
>
>
------------------------ Yahoo! Groups Sponsor --------------------~-->
Great things are happening at Yahoo! Groups. See the new email design.
http://us.click.yahoo.com/TISQkA/hOaOAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/