[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] surface area of the internal mass Vs building internal heat capacity
Internal mass is modeled as any other adiabatic heat transfer surface. The
"inside" surface of the internal mass has area (A) which interacts with the
zone by radiant and convection exchange, and it receives solar gains and
radiant gains from internal loads (electric equipment, people, etc.) just like
any other heat transfer surface. The "outside" surface of the internal mass is
assumed to be at the same temperature as the inside surface, and heat is stored
and released by the material layers. So, the area is used to determine the
thermal mass of the internal mass object, but it also impacts other heat
transfer mechanisms.
You said that you are using internal mass to change from a light building to a
heavy building. This will increase the interior thermal mass, but the exterior
walls will still be lightweight. A true "heavy" building would probably have
additional mass in the exterior walls as well.
Mike
On 10 Jul 2006 at 10:30, houcem mechri wrote:
> Hello every body
>
> I would like to know if the surface area of the internal mass is used only
> to calculate the internal heat capacity Cz because I find strange results when
> I change this surface area to obtain buildings from heavy to light.
> thanks.
>
>
> ---------------------------------
> Yahoo! Mail réinvente le mail ! Découvrez le nouveau Yahoo! Mail et son
> interface révolutionnaire.
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
See what's inside the new Yahoo! Groups email.
http://us.click.yahoo.com/2pRQfA/bOaOAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/