Re: [EnergyPlus_Support] Electric v/s Hot Gas Reheat



Merid,

As explained in the documentation, the maximum amount of heat reclaim 
for the COIL:Desuperheater:Heating is 30% of the total heat rejection. 
For your simulation, this must not be sufficient..... particularly at 
part-load conditions.  Yes, this could be real.  Did you compare the 
maximum heating capacity of your electric reheat coil to the maximum 
heat provided by your COIL:Desuperheater:Heating object?  No, there are 
no other aspects of the model that need to be modified.

UNITARYSYSTEM:HEATPUMP:AIRTOAIR and UnitarySystem:HeatPump:WaterToAir 
currently allow the user to specify both Blow through or Draw through 
fan arrangements. We intend to add draw thru configuration to the 
Unitary HeatCool systems in a future release (Oct 2006 or April 2007 
depending on scheduling).

Don

aboyemeplus wrote:

>Hi All,
>
>I am modeling a unitary system (type:Furnace:BlowThru:HeatCool)with 
>the high humidity control activated.
>First, I run the model with a Hot Gas Reheat Coil, then with an 
>electric reheat coil. The rest of the model remained unchanged. The 
>results from the simualtion using the electric reheat coil show that 
>zone temperature and humidity are tightly controlled. On the other 
>hand, the Hot Gas reheat simulation resulted in significant zone 
>temperature deviations from the cooling setpoint (zone is cooled as 
>much as 7 oF lower that setpoint temperature, to maintain desired 
>max humidity). This, in turn, required a much high system cooling 
>capacity. 
>
>Is this real? If not, are there any other aspects of the model that 
>need to be modified depending on which reheat coil type is used? 
>
>Also, are there any Unitary System Objects in EnergyPlus that 
>support a Draw thru configuartion for cooling and BlowThru for 
>heating?
>
>Your help is much appreciated.
>
>Merid 
>
>
>
>
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
>EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
> 
>Yahoo! Groups Links
>
>
>
>  
>




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/