Re: [EnergyPlus_Support] zone temperature error



It could be inadequate airflow, incorrect supply air temperature setpoints, 
incorrect chilled water setpoints, or a variety of other issues.  Is the 
chilled water supply temperature holding setpoint?  Is the supply air 
temperature holding setpoint?

Mike


On 14 Aug 2006 at 13:07, energypluser wrote:

> Dear all:
> As refer to the InputOutputReference, the zone control: thermostatic is in
> charge of 
> controlling the zone temperature. I set a dual setpoint with deadband object
> for my zone, 
> and my chiller have abundant capacity to serve the zone. But in the summer
> design day, the 
> temperature is out of the deadband. I have checked the schedules for the HVAC
> system and 
> the simulation results of the system. It seems that the system is operating in
> the design day. 
> How can I make the system supply enough cooling energy to keep the zone
> temeprature in 
> the deadband?
> Thank you in advance!
> 
> mac.cz
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
>  
> Yahoo! Groups Links
> 
> 
> 
>  
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/