[EnergyPlus_Support] Re: Humidifier Control
I found one problem with the file, it seems that the 10 KW latent gain
in the zone causes the major problems. To simulate a 10kw latent gain,
I have used the HOT WATER EQUIPMENT object and put in 10000W with 1.0
for fraction latent. Have I missed something about why I can't use
this object in this way? Is there any other way to introduce a 10kw
latent load without disrupting a humidifier's control?
Kind regards
-Elmer
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Elmer Morrissey"
<elmofuddly@...> wrote:
>
> Hello all,
>
> Could anyone take a look at a file I have uploaded in the problem
> submittals section (it's called "Test baseboard AHU3.idf"). As can be
> seen here, I cannot get the humidifier to turn on. I have looked at
> the outlet node's "humidity max" and it just returns zero constantly.
> Additionally, the "Zone/Sys Moisture Load Rate Predicted" looks out of
> sinc with the zone temperature and RH (RH setpoint is 60% but I only
> ever get 35% as the humidifier doesn't seem to turn on).
>
> I would really appreciate anyone's input.
>
> Kind regards
>
> -Elmer
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
> <mjwitte@> wrote:
> >
> > No, I do not see a way to accomplish this.
> >
> > Mike
> >
> >
> > On 16 Aug 2006 at 17:35, Elmer Morrissey wrote:
> >
> > > Hello all,
> > >
> > > Is it possible to turn on a humidifier in E+ but to have nodal
> control
> > > only and to ignore zone conditions. I need to raise the RH to
40% for
> > > temperatures of 26C.
> > >
> > > Kind regards
> > >
> > > -Elmer
> > >
> > >
> > >
> > >
> > >
> > >
> > > The primary EnergyPlus web site is found at:
> > > http://www.energyplus.gov
> > >
> > > The group web site is:
> > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > >
> > > Attachments are not allowed -- please post any files to the
> appropriate folder
> > > in the Files area of the Support Web Site.
> > >
> > > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf
> and press the
> > > "search" button.
> > >
> > > Yahoo! Groups Links
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> >
> >
> > ========================================================
> > Michael J. Witte, GARD Analytics, Inc.
> > EnergyPlus Testing and Support
> > EnergyPlus-Support@
> >
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.