Re: [EnergyPlus_Support] Low Temperature Radiant System Hydronic
To see the impact of undersized equipment, it should only be necessary to
change the purchased heating capacity. The load range should not need to
change.
For a simple model of opening windows, see the VENTILATION object. For a
detailed approach, see AIRFLOWNETWORK:*
Mike
On 31 Aug 2006 at 15:14, volkerbrendler wrote:
> Hallo Mike!
>
> thank you for your fast reply.
> After we set the value for the LOAD RANGE BASED object to a very high
> number the simulation runs quiet well.
>
> Additional we would like to simulate the zone temperatures in case of
> a too small designed heating power plant.
> For example we would like to limit the heating power. In that case we
> thought that our system only has to run for a longer time or even
> earlier to heat up our space.
> That means we have to limit, if this is possible, the purchased
> heating power -and- the load range based object .
>
> Another chance we see, is to use the Low Temperature Radiant System
> Hydronic:CONSTANT SPEED with limited power but without defining the
> supply temperature.
>
> The next thing we like to do is to control the infiltration in
> dependency to the zone temperature. We see in the output file that
> our summer temperatures are too high.
> For example, if the temperature rises above 24°C the infiltration
> rate should get a three times higher value than normal (like opening
> a window).
>
> Thank you in advance.
>
>
>
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/