Re: [EnergyPlus_Support] How do you disable modulation of opening factors?
Kendra:
What you have done is right to make all opening factors either 0 or 1.
Output results are also right at "timestep" report frequency.
There are two timesteps used in EnergyPlus: zone time step and system time
step. The zone time step is your input from the TIMESTEP IN HOUR object. The
system time step is used internally and is determined by zone temperature
difference between previous timestep and current timestep. If the difference
is more than 0.3C, the system time step is shorter than the zone time step.
The AirflowNetwork model is performed at the system timestep level. If you
use "detailed" reprt frequency, you can see opening factors are either 0 or
1.0. When "timestep" reprot frequncey is used, the opening factors are gived
as an average value over a zone timestep when system time step < zone time
step. That is why you see opening factors vary between 0 and 1.0.
Please let me know if you have more concerns.
Lixing Gu
Florida Solar Energy Center
----- Original Message -----
From: "colotupper" <kendra.tupper@xxxxxxxxx>
To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Wednesday, September 06, 2006 9:12 PM
Subject: [EnergyPlus_Support] How do you disable modulation of opening
factors?
>I am simulating Natural Ventilation with Airflow Networks and my
> Ventilation Control Mode = Temperature. I want to have only 2
> conditions: closed windows (opening factor = 0) and open windows
> (opening factor = 1). I have set Limit Value on Multiplier for
> Modulating Venting Open Factor = 1, and all opening factors equal to 1
> as well.
>
> For some reason, when i output hourly results, my Opening Factor and
> Opening Factor Multiplier for Venting Modulation vary between 0 and 1.
>
> I read past messages about this problem and tried changing my
> timesteps and reporting frequency, but this had no effect. Right now,
> I have my timestep set to 1 and my report frequency set to timestep.
> I also tried letting all of the fields default to disable the
> modulation, but this had no impact either.
>
> I am going to post this file - if anyone has any suggestion, I would
> greatly appreciate it!
>
> Thanks,
>
> Kendra
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate
> folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press
> the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
>
>
------------------------ Yahoo! Groups Sponsor --------------------~-->
Great things are happening at Yahoo! Groups. See the new email design.
http://us.click.yahoo.com/SktRrD/hOaOAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/