Re: [EnergyPlus_Support] radiant cooling with cooling sources
I have not tried in Energy plus yet. In reality, you shall have the follwoing set-ups for water side economizer:
1. Perimter system and interior system.
2. HX and anothe set of pumps to seperate the two water systems. Condensing water to serve the rediant panels for interior zone and perimeter zone for hot water system.
3. When HX loop is on, chillers are off and switch to cooling towers, the cooling towers shall be oversized to have enough capacity if you want to shut-off all your chillers.
Sue
Zhen Tian <tianzhen9@xxxxxxxxx> wrote:
Dear All,
I have a question about combining radiant slab cooling with differnt cooling sources. I try to link radiant cooling module to the cooling towers only. This strategy works well for cold climate. I also link radiant systems to central chiller (with water cooled cooling towers), which will works for hot area. But my question is, can I mixed the water from cooling towers and chiller ? So in the cold months, I will only use the water from cooling tower and in warm months the water will be the mixed water from the chiller and the cooling tower. Can anybody tell me how to configure the systems in EnergyPlus?
Thanks a lot in advance.
Regards,
Zhen Tian
[Non-text portions of this message have been removed]
---------------------------------
All-new Yahoo! Mail - Fire up a more powerful email and get things done faster.
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/