Re: [EnergyPlus_Support] Baseboard Heater:Water: Convective Model
> temperature, and Tin is the room temperature. I wonder if this Tin is
> the set indoor temperature or the obtained. In addition where plays
> the Max Flow Rate a roll in the calculation? Can you give me a short
> explanation about the model for the Baseboard Heater? Actually, how do
> the defined values, UA and Max Water Flow rate, influence the
> calculation algorithm?
Tin is the current calculated (obtained) zone air temperature.
Max Flow Rate is the upper limit on the hot water flow rate, which in turn
limits the heating capacity of the baseboard unit.
UA also limits the heating capacity.
Mike
On 9 Oct 2006 at 13:19, natasamdj wrote:
> Dear,
> Before some time I asked you about the model of Baseboard Heater. Then
> I got the answer that the model is not controlling return water
> temperature, rather it is controlling the water flow rate to add the
> required amount of heat to the zone to meet the thermostat setpoint.
>
> I have been reading about the model. I found out that the capacity of
> the heater is defined as q=UA*(Tw-Tin). Where Tw is the water inlet
> temperature, and Tin is the room temperature. I wonder if this Tin is
> the set indoor temperature or the obtained. In addition where plays
> the Max Flow Rate a roll in the calculation? Can you give me a short
> explanation about the model for the Baseboard Heater? Actually, how do
> the defined values, UA and Max Water Flow rate, influence the
> calculation algorithm?
>
> Thank you in advance!
>
> Natasa M.Djuric
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/