[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Re: Chiller Simulation



Ronald,

Yes, Could you post the file or send it to me at 
sankar.padhmanabhan@xxxxxxxxxxx

Thanks
Sankar

At 11:29 AM 10/19/2006, you wrote:

>Sankar,
>
>i am reporting to meter file, and asking for hourly frequency.
>The result of this, is a file with consumption during the period
>that i said i'd like the HVAC system to run, but the electricity
>consumption doesnt vary along the operational time. I've based my
>project in the example file for free cooling chiller, which runs
>only for the design day, so i adapted this to a annual run, and
>expected to have in report variation in power required for the HVAC
>system. Would you like me to post the file for you to check it?
>
>Thanks,
>Ronald.
>
>--- In 
><mailto:EnergyPlus_Support%40yahoogroups.com>EnergyPlus_Support@xxxxxxxxxxxxxxx, 
>Sankar
><sankar.padhmanabhan@...> wrote:
> >
> > Ronald,
> > I am still not clear, what you mean by saying "electrical
>consumption
> > is constant in the annual simulation". What are the values you are
> > reporting? What is the frequency of reporting? Are you reporting
>it
> > to meter file or the eso file? We would be able to help you if you
> > provide with a little more details. You can report the electricity
> > consumption to the meter file daily, monthly or for the entire
>runperiod.
> >
> > Thanks
> > Sankar
> >
> > At 09:53 AM 10/19/2006, you wrote:
> >
> > >Sankar,
> > >
> > >tanks for the your help, but i think i wasn't clear in my first
> > >email. My problem is because in the annual simulation, the report
> > >says me that the eletrical consumption is constant, and in my
> > >analisys i want a variable result, to have the period of the year
> > >that i spend more money.
> > >
> > >Thanks,
> > >Ronald.
> > >
> > >--- In
> > ><mailto:EnergyPlus_Support%
>40yahoogroups.com><mailto:EnergyPlus_Support%40yahoogroups.com>EnergyPlus_Support@xxxxxxxxxxxxxxx, 
>
> > >Sankar
> > ><sankar.padhmanabhan@> wrote:
> > > >
> > > > Ronald,
> > > > In order to do an annual simulation, you need to add a "RUN
> > >CONTROL"
> > > > object (allows you to turn on or off the sizing runs and design
> > >day
> > > > runs) and a 'RUN PERIOD" object in the input file. Refer I/O
> > > > reference for more details on this object. Also you need a
>weather
> > > > file to do an annual simulation.
> > > >
> > > > Thanks
> > > > Sankar
> > > >
> > > > At 09:22 AM 10/19/2006, you wrote:
> > > >
> > > >
> > > > >AnyOne,
> > > > >
> > > > >why the chillers simulated in example files are only for the
> > >design
> > > > >day? Can i simulate, for example a free cooling chiller, for
>the
> > > > >period of 1 year? How can i do this? Thanks.
> > > > >
> > > > >Ronald.
> > > > >
> > > > >
> > > >
> > > >
> > > > [Non-text portions of this message have been removed]
> > > >
> > >
> > >
> >
> >
> > [Non-text portions of this message have been removed]
> >
>
>


[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/