Re: [EnergyPlus_Support] Preheat Coil Operation
I tried to reproduce the problem by adding preheat to example file CompactHVAC-
5ZoneVAVWaterCooled.idf, but the preheat coil puts out 7.2C, even with 100% OA
on the winter design day. Please post the file in the yahoo file area or send
zipped to energyplus-support@xxxxxxxx.
Mike
On 14 Nov 2006 at 22:36, asheaffe wrote:
> I am simulating a COMPACT VAV system that has a preheat coil due to
> the large amount of OA that my zones require. I have the gas preheat
> coil set to deliver 7.2C minimum to the system. However, during the
> simulation, the outlet temp of the coil regularly fluctuates below
> that temp. In fact during the design day it stays at -3.5C. The
> schedule for the coil is currently blank, meaning it should be
> available all the time. Any ideas on what might cause this? I can
> post the file, if there are no quick fixes.
>
> Thanks,
>
> Andrew
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/