Re: [EnergyPlus_Support] Interzone surface and Windows compositions.



1.  Not really.  You can define two zones without a dividing surface, but there 
will be no exchange between the zones where they meet.  If you add an interzone 
window, you can pass solar gains from one zone to the next.  And if you add 
MIXING or CROSS MIXING, you can create an air exchange between the zones.  But 
there is no radiant exchange from one zone to the next.  For your state pupose 
of reporting thermal comfort for two locations, it would be better to model the 
two areas in the same zone and use 2 different PEOPLE objects. By using Angle 
Factor List(s), you can change the mix of surfaces which each PEOPLE object is 
affeted by.  Note that solar gains incident on the PEOPLE are not included in 
the thermal comfort models.  Only the inside surface temperature of the window 
impacts the reported thermal comfort values.

2.  In EnergyPlus, all windows must be modeled as a subsurface 
(Surface:HeatTransfer:Sub) place on a base surface (Surface:HeatTransfer). If 
you make the base surface material match the properties of the frame, then you 
can place windows on the base surface cover almost of the surface (but there 
must always be a small amount of base surface area remaining).  For the facade 
with dividers, you can either place multiple windows on the base surface, or 
place one large window and use WindowFrameAndDivider to add the dividers.  Note 
that the frame area of WindowFrameAndDivider is added outside the 
Surface:HeatTransfer:Sub area.

Mike


On 14 Nov 2006 at 18:54, Thiago Karashima wrote:

> Hi,
> 
>     I´m starting the characterization of a 10 sotories building and 
> at this point i have two questions:
> 
> 1) Is it possible to create two contiguous zones in such a way that 
> there is no surface dividing these two zones? I want to do this to 
> visualize the difference between thermal comfort of those people who 
> works next to the windows and those who works in the core of the 
> building, away from sunlit windows.
> 
> 2) Do someone have any idea how can i model the two facades of my 
> building? One facede area is almost 100% glass, the other is 
> composed of a frame and divider that is part glass and part metal 
> sheet. I´ve uploaded some pictures in the group website; they are in 
> the link "Photos", in a Photo Album called "ThiagoKarashima".
> 
> I would appreciate any kind of sugestion.
> 
> Thank you for your patiance!
> 
> Thiago Karashima
> LaAr - www.laar.unb.br
> University of Brasília - Brazil
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
>  
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/